Grounding station vs Vertical Antenna and tower

Oct 28th 2018, 12:56

VE3SR

Joined: Mar 2nd 2014, 00:20
Total Topics: 0
Total Posts: 0
Have a question and asking for information/opinion on using the same ground for the station equipment with the tower. Currently running a cable to the ground rod and tower, then to an additional series of grounds each 8 feet apart and 8 feet deep - 8 additional grounds.

The next issue is if I used the tower as a 160 meter shunt fed tower. Should the tower ground be separate from the station ground and the series of ground rods.

Or is it permissible to attach all ground systems beginning at the tower as a single ground system for the entire station as it is currently without a shunt fed tower
Oct 29th 2018, 10:26

W1VT

Joined: Apr 4th 1998, 00:00
Total Topics: 0
Total Posts: 0
https://www.rack-a-tiers.com/16136/cec-versus-nec/
According to the CEC a grounding conductor is the main electrode driven into the ground, which protects the electrical equipment from overloading when a power surge occurs or lightning strikes the electrical wires. This would be called a grounding electrode conductor by the NEC.

According to the NEC a grounded conductor is a wire which runs through the electrical system, commonly referred to as a neutral wire, and serves as a current return path for electrical services. This is what the CEC refers to as an identified conductor.

You need to have an entrance panel where all the conductors entering the station are bonded together. I got a call from someone who had a lot of damage from lightning because he neglected to do anything with the rotator cable. I have gas discharge tubes between all the rotator cable wires and the copper plate that I use.

You need to bond all the grounds together. If they aren't, lightning can cause a lot of damage getting to the best ground to make its exit. Especially if it travels through the house to get there.

The ARRL Grounding and Bonding book may help you.

Zak W1VT
ARRL Senior Lab Engineer

Oct 29th 2018, 20:08

WA0CBW

Joined: Apr 4th 1998, 00:00
Total Topics: 0
Total Posts: 0
Normally ground rods are spaced twice their length apart. 8-foot ground rods would be placed 16 feet apart for maximum effectiveness. The NEC also requires all external ground rods be connected to the building main electrical ground.